Short/long press dimming #
This script works as a standard KNX push-button
where short press sends either ON or OFF
and long press performs 4-bit dimming.
For this to work the control button must have a
start-stop behaviour - ON is sent when the button
is pressed, OFF is sent when it is released.
Create a resident script with 0 sleep time,
modify the timeout and mapping variables as needed.
Default long press time is 1 seconds.
In this example there are two input objects - 0/0/3 and 0/0/4.
If 0/0/3 is pressed and released within 1 second then OFF
is sent to 0/0/1 (short press on/off).
Otherwise DIM DOWN is sent to 0/0/2 (long press dimming).
When the button is released then DIM STOP is sent to 0/0/2.
If 0/0/4 is pressed and released within 1 second then ON
Otherwise DIM UP is sent to 0/0/2 (long press dimming).
if not client then
timeout = 1 -- long press in seconds
mapping = {
['0/0/3'] = { onoff = '0/0/1', dim = '0/0/2', on = false },
['0/0/4'] = { onoff = '0/0/1', dim = '0/0/2', on = true },
timerstep = timeout / 4
function eventhandler(event)
local object = mapping[ event.dst ]
if not object then
return
local value = busdatatype.decode(event.datahex, dt.bool)
if value then
object.timer = timeout
elseif object.timer then
if object.timer == 0 then
grp.write(object.dim, object.on and 8 or 0, dt.bit4)
grp.write(object.onoff, object.on, dt.bool)
object.timer = nil
client = require('localbus').new(1)
clientfd = socket.fdmaskset(client:getfd(), 'r')
client:sethandler('groupwrite', eventhandler)
timer = require('timerfd').new(timerstep)
timerfd = socket.fdmaskset(timer:getfd(), 'r')
res, clientstat, timerstat = socket.selectfds(10, clientfd, timerfd)
if res then
if clientstat then
client:step()
if timerstat then
timer:read()
for addr, object in pairs(mapping) do
timervalue = object.timer
if timervalue and timervalue > 0 then
timervalue = math.max(0, timervalue - timerstep)
if timervalue == 0 then
grp.write(object.dim, object.on and 9 or 1, dt.bit4)
object.timer = timervalue