Modbus JSON profile reference #
Global profile fields #
manufacturer
Manufacturer name. string, required
Example: Embedded Systems
description
Device description or model name. string, required
Example: Universal 16+4 I/O module
timeout
Overrides default response timeout of 0.5 seconds for RTU or 3 seconds for TCP. number
product_code
Product code which can be used for automatic profile mapping. string
Obtained from the device via read device identification object id 1 request.
read_swap
Sets global byte/word swap order during conversion (endianness). boolean/string
Same as read_swap field from mapping.
read_delay
Delay in seconds (max 1 second) between consecutive read requests from the slave. number
Should only be used if consecutives reads result in a timeout error.
write_delay
Delay in seconds (max 1 second) before write is sent to the slave. number
Should only be used if consecutives writes result in a timeout error.
Mapping fields #
name
Datapoint name. string, required
Example: Output 2
type
Modbus datapoint type. string, required
Possible values:
coildiscreteinputregisterinputregister
address
Datapoint address (0-based). number, required
datatype
Modbus value data type. Read length is chosen based on data type, except for string type where data length must be specified manually in the read_count field. string, required
Possible values:
uint16int16float16uint32int32float32uint64int64float64quad10ks10kstring
bus_datatype
Mapped object data type, key from dt table string/number, required
Possible values:
boolbit4uint8scaleangleint8uint16int16float16temperaturetimedateuint32rgbwint32float32stringint64uint24rgbtext
writable
Set to true to enable writing to coil or register boolean
write_only
Set to true to disable reading coil or register value when writable is enabled. boolean
write_multiple
Set to true to force writing using multiple coil/register write function (code 16) even when writing to a single coil/register. boolean
value_delta
New value is sent when the difference between previously sent value and current value is larger than delta. Defaults to unset, send on any value changed. number
value_base
Add a specified number to the resulting value. number
value_multiplier
Multiply the resulting value by a specified number. number
Value calculation: value = value_base + value * value_multiplier
value_bitmask
Bit mask to apply when reading and writing. number
Shifting is done automatically using the Count Trailing Zeros (CTZ) function.
Example: if value = 0xABCD and mask = 0x0F00 then CTZ(mask) = 8
The resulting value is (value & mask) >> 8 = 0x0B00 >> 8 = 0xB
write_bitmask
Set to true to enable writing shifted value to the register using value_bitmask boolean
Only uint16 datatype is supported.
value_nan
Array of 16-bit integers. array
If specified and read operation returns the same array then no further processing of value is done.
value_custom
A list of key → value mapping. object
Example: { "0": "Off", "1": "Low", "2": "Medium", "3": "High" }
value_default
Default value that is sent when coil/register cannot be read. boolean/number
internal
Not visible to the user when set to true, should be used for scale registers. boolean
units
Object units/suffix. string
address_scale
Address of the register containing value scale factor. number
Value calculation: value = value * 10 ^ scale
read_count
Number of registers to be read at once. number
Can be used for devices that only support reading of a specific block of registers; up to 125 registers can read at once.
Required for string data type.
read_swap
Swap byte/word order during conversion (endianness). boolean/string
Default value is word (2-byte) swap.
Possible values:
n(no swap = 0xABCD)w(word swap = 0xCDAB)b(byte swap = 0xBADC)bw(byte and word swap = 0xDCBA)
read_offset
Position of the first coil/register in the data from the block of registers (0-based). number
bus_address
Group address of mapped object. group address as a string
Recommended to use only during development.